Industry Online Support
Technical Forum
9/21/2009 9:45 AM | |
Joined: 10/9/2007 Last visit: 5/25/2023 Posts: 1204 Rating:
|
Hi Lonelynx Take a look at these documents http://siemens.siprotec.de/download_neu/devices/1_General/Doku_Protokolle/Englisch/Profibus%20DP/SIPROTEC4_PROFIBUS_DP_FAQ_en.pdf http://siemens.siprotec.de/download_neu/applications/communication/PCS7v6_Siprotec_7SJ6x_Mapping3.4_v1.0_en.pdf It's not possible to change the Mapping in Siprotec, so you cannot used a smaller quantity of bytes. I think the solution is to install more Y-Links. Mike J |
Energy Automation products: Sicam, Siprotec, Digsi |
|
This contribution was helpful to
1 thankful Users |
9/30/2009 9:34 AM | |
Posts: 5 Rating:
|
Thanks Mike Y-link will be the solution Best Regards |
Follow us on