Dear All I want to know how can i check the status of profibus Dp connected .need help on this Regards |
3/16/2014 6:09 PM | |
Posts: 8946 Rating:
|
Hard for me to understand what you want. First advice: have a look at SFC51. |
3/17/2014 6:32 AM | |
Joined: 1/21/2013 Last visit: 4/21/2023 Posts: 4617 Rating:
|
Hello Mr Khan, second advice: http://support.automation.siemens.com/WW/view/en/26996747 How do you find out the status of the stations of a DP master system or |
Last edited by: Ste39 at: 3/17/2014 6:37 AM |
|
3/17/2014 8:58 AM | |
Joined: 1/21/2013 Last visit: 4/21/2023 Posts: 4617 Rating:
|
Hello Mr Khan, Why not use this: This is with SFC 51 like IBN-Service mentioned: How is a DP slave's diagnostic data read out with SFC 51 "RDSYSST" (with an integrated DP interface on the CPU as the DP master)? This is with SFC13: How do you read out the diagnosis data of a PROFIBUS DP slave with the SFC13 "DPNRM_DG" and how do you evaluate the data in the user program? |
Last edited by: Ste39 at: 3/17/2014 9:05 AMLast edited by: Ste39 at: 3/17/2014 9:02 AM |
|
3/17/2014 11:38 AM | |
Joined: 10/3/2008 Last visit: 5/30/2023 Posts: 936 Rating:
|
Hi, if you want to see it in WinCC: http://support.automation.siemens.com/WW/view/en/10343086. => Systemdiagnostics Wüstenräuber |