4/1/2012 4:03 PM | |
Joined: 12/22/2006 Last visit: 1/25/2022 Posts: 1742 Rating: (309) |
Hello, I would use list 0694 as dscribed here: How do you find out the status of the stations of a DP master system or of a PROFINET IO system?: http://support.automation.siemens.com/WW/view/en/31895566 You will get one bit per slave. 1 = not OK |
Best regards |
|
4/1/2012 4:56 PM | |
Joined: 1/28/2009 Last visit: 1/19/2025 Posts: 6858 Rating: (1366) |
Hello , Also check the samples here: I wanna know when DP Slave has a failure - OB86Best regards, Hamid Hosseini |