Good day. 7 Lenze drives are connected through profibus to cpu 313-C2DP. hmi on the mpi. Startup stage seems to be ok. Machine running fine for couple of hours. Then suddenly 1.some drives output get freezed (hmi fields value) for some time. 2.any one of the drives giving the faulty signal through profibus, no physical alarm or fault on drive itself. plc show SF and stopped. if plc is restarted everything is ok as before. we have to figure out the reason and get rid of it or bypass it safely if possible to ensure discontinued operation. so, downloaded OB85 to plc to ignore io access process image update error, but it is not a safe practice, is it? Cause of error may be interference of profibus cables. but we checked those visually and find nothing wrong. please someone shed some light on why SF is coming, is it ok to download OB, what could be the reasons for profibus communication interruption? Attached is diagnostic buffer for your consideration. thank you. AttachmentModule Information - Copy.pdf (63 Downloads) |
8/5/2013 12:32 PM | |
Posts: 11 Rating:
|
Thanks for the suggestion. We will try to remove the root cause. Meanwhile we have to depend on OB handling the brief interruption on the bus. Regards |