The PI (organisation for PROFIBUS and PROFINET) defines a PROFIdrive profile. In this the control word 1 is defined. You will first have to set several enables and then give the ON-command. Generally you have to send 047E to set all enables and then switch to 047F to switch on the drive. If the enables and the ON command comes at the same time, the drive will not switch on! Download the manual at https://support.industry.siemens.com/cs/ww/en/view/94020562 and look in chapter 7.3.1.1 . Even if you have a other drive, the Bits 0 to 10 are identic. |
|
|