9/11/2008 2:21 PM | |
Posts: 1 Rating: (0) |
Hi All, I am using WinCC v6.2 for my project. I want to include dynamic texts like username or computername in the event messages. I have attached the file so that you can understand how the alarm control window should look like in runtime. Here the "Vaitk:" is the operator who is making some operation from HMI. Similarly it should also reflect which operator is acknowledging alarm messages from HMI.
Following things I have already tried ..but it is not working. 1) In the event class properties->acknowledgement tab "Comments assigned to the unique user" and "Comments always in the mesage list of the incoming message" checkboxes have been checked. 2) In the Message blocks-> System blocks, username block have been selected. 3) In the "WinCC message text" field of the Alarm Logging Table window the messages are written like "@102%s@: hyd prs pump 01 rem sel". The @102%sis for the user name and rest is the event message. 4) In the CCAlgWinCtrl-> message block tab the the username checkbox have been selected. During runtime I get the event messages except the dynamic text i.e the username. The message displayed is ": hyd prs pump 01 rem sel". Pls check the attached file for the settings I have made. AttachmentAlarm Settings.pdf (135 Downloads) |
Last edited by: rahuldev at: 9/11/2008 2:23 PM |
|
9/17/2008 12:49 PM | |
Posts: 1776 Rating: (95)
|
Hi, have you seen this FAQ http://support.automation.siemens.com/WW/view/en/25166621 |