Joined: 3/30/2020 Last visit: 12/24/2024 Posts: 5014 Rating: (1026) |
Though you are correct, there is a workaround that can be considered. (Only recently an old topic was re-opened which presents the idea.) The idea is to preconfigure hardware configurations that would possibly be used. The PLC will then boot up to the appropriate hardware configuration option. This is an option with limitations, but it can work. The alternative is to use external signal converters. It make the system more expensive BUT they can be made configurable and the PLC is isolated from the field (!). |
Activities of this user is voluntary. There is no obligation or liability placed on this user. Though optional, your 'please' and 'thank you' is highly valued. |
|
This contribution was helpful to1 thankful Users |
6/15/2020 1:38 PM | |
Joined: 9/19/2011 Last visit: 1/17/2025 Posts: 140 Rating: (33) |
Hello Qwazee, I do not believe that S7-1200 system supports the configuration option listed in your link. Larry |
6/15/2020 1:44 PM | |
Joined: 3/30/2020 Last visit: 12/24/2024 Posts: 5014 Rating: (1026) |
Hi Larry. The S7-1200 does have configuration control. You may find the attached document of interest. It is an extract from the official S7-1200 manual. Regards. AttachmentExtract-Configuration-Control.pdf (210 Downloads) |