4/28/2017 7:13 AM | |
Posts: 3 Rating: (0) |
Dearnulizhang
1) The power supply can not be tested alone - without filter - ? 2) Is this - (non existence of filter) - the reason for the voltage boost/increase in power supply ? 3) If I use original filter - which we had ordered and received today - my problem of voltage increase will be solved ? |
Last edited by: shant at: 4/28/2017 7:21:33 AM |
|
4/29/2017 12:52 AM | |
Joined: 10/17/2007 Last visit: 4/27/2024 Posts: 3974 Rating: (340) |
#1--The power supply module can be tested alone , but only basic test don't connect so many drives, special NOT connect big spindle drive. #2--I don't understand youe question for voltage increase --what do you mean? what is your Mains 3 AC V==? . Balance is most important--Vlotage from 380 to 480 V all goo, but you need check setting DIP switch on top of PS module --follow the Siemens book or new version PS, there is yellow stick on the front of PS module #3--for your 36/47KW PS, there are Reactor (Chock) and Filter. some time you use 2-in-1. The Chock is the must, the filter is an option, if you cannot use matched filter--it is better DO NOT use filter--NO filter is better than use wrong filter
|
If you like my comments please |
|