6/6/2011 7:54 AM | |
Joined: 5/28/2008 Last visit: 4/15/2024 Posts: 4505 Rating: (835) |
Hellolordgalen,
AttachmentBA_6EP133x-3BA00_C98130-A7548-A001-08-6419_201009.pdf (76 Downloads) |
Ayman Elotaify |
|
6/7/2011 8:36 AM | |
Joined: 4/22/2010 Last visit: 5/19/2023 Posts: 82 Rating: (1) |
Hi Aret, Thanks again...I forgot to attach the wiring diagram..Im going to attached it now for you to review if you have time..Please refer to the condition stated above... Thanks and best regards, lordgalen
AttachmentSAMPLE WIRING DIAGRAM.pdf (92 Downloads) |
6/7/2011 8:49 AM | |
Posts: 2348 Rating: (263)
|
Well, it's standard wiring diagram, so everything i said above is true Please write MLFB number for your DI module |
6/7/2011 11:41 AM | |
Joined: 9/7/2007 Last visit: 8/30/2023 Posts: 550 Rating: (61) |
Hilordgalen, I faced this problem previously, I used: 1) DI module: 6ES7 321-BL00-0AA0 2) Front Connector:6ES7 392-1AM00-0AA0 3) Bus Unit:6ES7 195-7HB00-0XA0 An external short circuit happened, 380 V AC from the MCC passed through the signal cables, as a result the front connector melted!!! The DI module was destroyed because the short circuit had made a big hole in the plastic casing of the module, finally the electrical circuit inside the Bus unit was damaged and we replaced all the three items. Nothing else was damaged |
Best Regards |
|
6/9/2011 5:33 AM | |
Joined: 4/22/2010 Last visit: 5/19/2023 Posts: 82 Rating: (1) |
Thank you so much experts.... |