Joined: 4/22/2010 Last visit: 11/18/2024 Posts: 5697 Rating: (715)
|
Hello, In addition to this good information i have attached part of the Logo_manual. If you are sure all is connected well, you can try to Clear the alarm. Regards, Marcjan Attachmentlogo_Diagnosing errors.pdf (289 Downloads) |
Problem solved? |
|
This contribution was helpful to1 thankful Users |
6/13/2014 1:13 PM | |
Joined: 10/16/2012 Last visit: 9/18/2024 Posts: 12 Rating: (0) |
Hallo William B. and Marcjan Thank you very much for helping me to solve this problem. This forum is very helpfull. Yes the EM is for the Exspansion Module. The fault that caused this was the following: In the program for my client I have used only a basic 0BA7 module with NO exspansion modules connected to it, but in my software program I was using seven output and not four. This caused the program to go into error mode as it could not see the output on my exspansion module. I have deleted that section of the program and now the error disappeared Thanks again for all you help Herman |
This contribution was helpful to1 thankful Users |