9/24/2021 1:06 PM | |
Joined: 3/27/2008 Last visit: 2/12/2025 Posts: 1166 Rating:
|
Try this, using BICO if you are familiar with this. |
Tractor |
|
This contribution was helpful to
1 thankful Users |
9/24/2021 1:13 PM | |
Joined: 3/27/2008 Last visit: 2/12/2025 Posts: 1166 Rating:
|
This may look better for access: Using BICO, using a run switch the operation described below: Operation: Parameter P2900 = 20%, with scale of 0/10 Volts into terminals ¾, this is set to 20%, which is 2Volts. When analogue input 0, is greater than 2Volts the output QL goes high. AND input is fed to P20030, and if the RUN command is high, closed switch, the output of the AND gate sends a run command, as P840 is set to r20031. Tractor AttachmentHibernate G120.docx (311 Downloads) |
Tractor |
|
9/27/2021 12:36 PM | |
Joined: 6/20/2018 Last visit: 1/20/2025 Posts: 41 Rating:
|
Hi, but its possible to do it in TIA portal or i need the console of g120? |
9/27/2021 12:49 PM | |
Joined: 8/21/2018 Last visit: 1/29/2025 Posts: 91 Rating:
|
It should be possible. I think You should choose option "Display extended parameters" in drive parameter window. |