Hello, the safety integrated settings could not be changed with DDS or CDS. So in case you have selected safety integrated via PROFIsafe, this will be the same no matter what CDS is selected. Are you using encoderless safety integrated extended functions? If so you have to consider that the drive will activate STO internally under certain circumstances. You can find more detailed information in chapter 6.6.5 of the G120 saftey integrated manual. https://support.industry.siemens.com/cs/ww/en/view/109757227 When just using safety integrated basic functions via onboard terminals the topic mentioned above is not relevant and you should be able to JOG the drive. |