Hello medaadi, you should observe that the last and first station must be always powered on, because the termination is using pull up/pull down resistors. If you restart a Panel it is not fully guaranteed, that the ASIC is in operation based on reset signal. If this appears your Profibus Network will go down. As response you will have for a short time no communication. As solution for this you can use a active bus termination Bus terminating elements for PROFIBUS subnetworks In your configuration you wrote only panels connected to the network, there are also other stations connected? |