7/4/2013 5:04 PM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
Hello, Alarm 25080 is positioning monitoring. Do you have scale or motor encoder as feedback? Please check it. |
7/5/2013 8:09 AM | |
Posts: 14 Rating: (0) |
Motor Encoder |
7/5/2013 11:20 AM | |
Posts: 14 Rating: (0) |
Thank you - can you give me directions how to check/modify the MD? thanks, Daniiel
|
7/5/2013 6:26 PM | |
Posts: 14 Rating: (0) |
I dont find it, attached the controller we have, thanks
|
7/6/2013 8:35 AM | |
Posts: 14 Rating: (0) |
Reference - not possible as we got same allarm as when trying to move only Z; the procedure for refernece - starts with Z axis;
|
7/6/2013 10:27 AM | |
Posts: 14 Rating: (0) |
MD36010 0.1 deg MD36020 1 s MD32200 1 userdef
|
7/17/2013 12:03 PM | |
Posts: 14 Rating: (0) |
Once again thank you, please advise the procedure to verify the power module, thanks, Daniiel
|
7/17/2013 12:29 PM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
Hello, Please find attached file which explaines how to check power module. It is mainly to check & confirm the healthiness of IGBT module. Please checkfor anyunbalance in resistance, since from the nature of problem, it is sure that there is no short circuit in IGBT. AttachmentChecking the power module.pdf (301 Downloads) |
This contribution was helpful to2 thankful Users |
7/21/2013 8:13 AM | |
Posts: 14 Rating: (0) |
Thank you, Daniiel
|