9/28/2018 5:27 AM | |
Posts: 66 Rating: (0) |
Hello Mr.Christoph, Please find attached pdf containing images for your reference. I have assigned D410-2 as IO device and 1515-2 PLC as Controller. Till the D410 goes to run mode, i see there is User data failure of D410 hardware component alarm in the PLC diagnostic buffer. With reference to the image, i have used _mc_Readactualposition block in the program. When i use 1 in the enable bool, i am able to clear all the error and able to execute the program. But when i use a predefined IO, i couldn;t go to run mode after download of the program. And then the alarm occurs "Error occured while reading system or I/O variables" in the D410 diagnostic buffer. How to use I/O (PI XX.X, PID XXX and PQD) directly in the ladder program? I had created a time delay in startup too. So change in the errors. Also refer the MCC program. I have used Wait for signal using I/O signals and no errors. The program is running well. AttachmentIO_Variable_Error.pdf (341 Downloads) |
Last edited by: Kripaharan at: 9/28/2018 5:59:08 AM |
|
10/2/2018 6:26 AM | |
Posts: 66 Rating: (0) |
Hi Mr.Christoph, Please find attached diagnostic buffer file. After adding and I/O in the MC reset function, the IO error occurred and i couldn't made to Run mode and then PLC goes to Error mode. I have attached the diagnostic buffer error of both PLC & D410 IO device. Also i have attached diagnostic buffer of both PLC & D410 after removing IO from MC reset function and changing to run mode. PLC is going to error state because of D410 device in error state. Please guide me. AttachmentSimotion_Diagnostics_Buffer_during_error.zip (299 Downloads) |