10/22/2015 10:32 AM | |
Posts: 15 Rating:
Good day! I have a similar problem. I add drive to the double modul unit. I do commissioning of the servo drive 1FK7. Stumps click on the green button pops up an error "switch-on disable active (iscoa: 30020)." The parameter p9 and P10 - 0 (ready). Tell me, who knows where to find the cause of the error. CU CU320 Duble motor modul 6SL3120-2TE21-0Axx P.S. Can this problem occurs because the second drive into module has a value of r2 - 00 (Always On) ------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 10/22/2015 1:41:40 PMNew subject after splitting |
10/22/2015 11:34 AM | |
Posts: 15 Rating:
In tab alarms, no messages, only warnings related to other drives. |
10/22/2015 11:35 AM | |
Posts: 15 Rating:
Tab alarm. |
10/22/2015 11:59 AM | |
Posts: 1529 Rating:
do you have a hard-wired Emergency Stop open? I get that when the Pulse Enable is open. |
Posts: 15 Rating:
And screenshot of the second servo motor in this double motor unit |
10/22/2015 12:06 PM | |
Posts: 15 Rating:
Du you mean the connector x21 3-4? |
10/22/2015 12:09 PM | |
Posts: 1529 Rating:
yes. For a DMM, there is also an X22. Both need to be connected to 24V |
10/22/2015 12:14 PM | |
Joined: 5/12/2006 Last visit: 2/6/2023 Posts: 21222 Rating:
Hello, if x21 is missing but needed then the r046.08 should be set.
Christoph |