11/21/2024 7:21 AM | |
Joined: 1/4/2007 Last visit: 12/2/2024 Posts: 1152 Rating: (175)
|
Hello Anya_p26, In the Siwarex M module, the RAM is buffered with a capacitor. Maybe this capacitor was empty due to the long power off of the Siwarex M module. You can acknowledge this error message by sending the DR43 from the PLC to the Siwarex M module OR you can acknowledge this error message by using the Siwatool software. If you need the Siwatool software, write an email to: hotline.siwarex@siemens.com If you want, you can replace the Siwarex M module with the Siwarex FTA module. But here, you have to change your Step7 program, see also the attached file, please. Best regards Siwarexi
AttachmentSIWAREX_M_to_SIWAREX_FTA-ENG.pdf (7 Downloads) |