7/7/2009 5:54 AM | |
Posts: 116 Rating:
|
Hi, I am using CPU 315-2DP with Profibus interface. At the time of online monitoring if Input and Output words I came across some error. Please find the attached screen shot of the same. Can anyone tell me cause of this error and how to remove this? Thanks Paresh AttachmentSimatic_Error.zip (48 Downloads) |
7/7/2009 6:02 AM | |
Posts: 691 Rating:
|
Try with PEW and PAW if these are analog values |
Last edited by: Ninja Robot at: 7/7/2009 6:04 AM |
|
7/7/2009 6:12 AM | |
Posts: 116 Rating:
|
Hi Ninja, These input and output words of Profibus slaves not an analog modules. Regards Paresh |
7/7/2009 6:47 AM | |
Joined: 10/7/2005 Last visit: 6/1/2023 Posts: 2966 Rating:
|
Hello Paresh There is a limit as to how many Variabels you can monitor and/or modify at the same time in a VAT (the error message actually says it all). Try to modify less variables or have a second VAT open (arrange two VAT's side by side if you wish)to overcome this "problem". |
Cheers |
|
7/7/2009 7:26 AM | |
Joined: 5/28/2008 Last visit: 6/2/2023 Posts: 4448 Rating:
|
Hello, The same subject has been alread disscussed here: Max. number of Actual Params That Can Be Monitored |
Ayman Elotaify |
|
7/7/2009 10:26 AM | |
Posts: 116 Rating:
|
Hi Fritz, Can we open more than one VAT window? Regards Paresh |
7/7/2009 10:46 AM | |
Posts: 691 Rating:
|
Yes you can open 4-5 VAT tables at a time |
7/7/2009 11:08 AM | |
Posts: 116 Rating:
|
Thanks ninja I will try this option and let you know. Regards Paresh |