Hello 1.You wrote: " We have system with ES/OS Server + 2 OS. 3 Computer: ES1, OS1, OS2. Project we have: ES1 - WinCC Application - ES1" I don't know the PCS7 version but I suppose it's 7.0 or 7.0 SP1. It's not usual (and not approved by Siemens)to have a serverin ES. Please see Tables 1 and 3 (itens C.2.1 and C.2.3) in the document below
Maybe you mean an Single Station running in ES. Then it's ok. 2. You wrote: "And if we open with right click Object Properties from ES/OS -> Target OS -> Path to the Target OS Computer is empty, how we should configure it?" You must not configure because you cannot download to the same computer. If you have a path to a folder in the same computer and try to download a error message will happen. So you must open the OS (in your project)and run it (normally you do this way in Single Station ES/OS projects). 3. You wrote: "But we haven't been able to download OS's to OS PC's. PLC -> Download causes this error. RT Station not obtainable." Probably you're trying to download canges but the OSs are not running. Then the ES cannot find the WInCC runtime working. You can download the complete OS project when the OSs are stopped or changes when they're running. Try to download the Complete OSs. The OS in Es must be closed. Good luck. Regards. Mario |
||