Joined: 1/15/2009 Last visit: 4/6/2025 Posts: 316 Rating:
|
Hi Mihal, Why is Station Configurator empty? For PCS7 this should be populated via PLC-> Configure/Download from the ES in the multiproject to itself (please see the PCS7 Compendium Section 3.5.1 Engineering Station for procedurehttp://support.automation.siemens.com/WW/view/en/63187279) After Station Configurator is populated (and connections downloaded via netpro) you should be able to Start Lifelist or open a device in PDM via HW Config.
|