4/1/2013 7:28 AM | |
Posts: 15 Rating:
|
Hi, Does this example which you have mentioned can be used for allen bradley PLC which uses Ethernet IP protocol. I have to establish communication between S7 1214C and L32E compactlogix processor of AB. |
Last edited by: O_Moderator at: 4/4/2013 10:29 AMnew subject after splitting from /tf/WW/en/Posts/46768#top |
|
4/1/2013 7:59 AM | |
Joined: 8/31/2010 Last visit: 4/24/2025 Posts: 1525 Rating:
|
Hello kri2020, Ethernet IP is different from TCP/IP. TCP/IP is a open protocol which is supported in S7-1200. So you can not make use of that sample program to communicate a S7-1200 with AB L32E. Possibility to communicate a S7-1200 and AB PLC is via a protocol which is supported in both the system (S7-1200 Protocols) or else a Gateway must be employed. |
Like it? Rate it! |
|
This contribution was helpful to
1 thankful Users |
4/1/2013 9:36 PM | |
Joined: 7/7/2010 Last visit: 4/24/2025 Posts: 15816 Rating:
|
This web pdf [ http://arxiv.org/ftp/cs/papers/0110/0110065.pdf] explains some of the details as well as provides good references at the end. In my specific case, I was modifying and customizing an interface with a non-AB device to communicate properly using what is similar to the GSD/GSE configuration file in the Siemens S7 world. I had to then make the non-AB device communicate using that custom configuration (something the vendor said could not be done - and in the end, it worked very well.) The references on ethernet/ip is what you will be looking for. If you find the amount of plc programming is too involved, you can get a profinet adapter for your L32E, or does it already support Profinet with proper licensing? It might be similer to use Modbus/TCP as that is provided with the s7-1200 and should be an option on the L32E, perhaps as a library module. |
Last edited by: huggy_d1 at: 4/1/2013 9:44 PMscience guy |
|