i would like to establish communication between S7-300 and communication module cp340- rs232 so that i can use it as modbus to connect with pm240 inverters .i have cpu 314c-2dp model . please tell me how .
------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 7/4/2017 12:32:05 PMNew subject after splitting |
|
7/3/2017 1:50 PM | |
Joined: 9/27/2006 Last visit: 3/17/2025 Posts: 12344 Rating:
|
Hello m. tahboub; With a S7-300 CPU and a serial CP (RS-232 in our case) you can setup Modbus RTU connexions; is that what you need to do? The Modbus RTU master (or slave) for a S7-300, as developped by Siemens, requires a CP 341, with a loadable driver for Modbus RTU and a physical dongle inserted in he CP module. You could not do it with a CP 340. However, member Tibi68 has proposed a solution for the CP 340, which you can download here: MODBUS RTU MASTER FOR CP340/341/441-X (NO DONGLE REQUIRED) You do not require the Siemens Modbus driver for this; on the other hand, you will get no support from Siemens,only from Tibi68 directly, through the link above. Hope this helps, Daniel Chartier |