11/25/2015 8:52 AM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating:
|
hi dimas, have a look to following manual on page 103. this should be the table for S7-1500 with S7-400(not S7-300/S7-400 like in the headline): CPU-CPU Communication with SIMATIC ControllersFor S7-Connection you could use "USEND/URCV", BSEND/BRCV, "PUT, GET", and also Open Communication should work. Please note that PLCSim is not an real CPU and not every function does work on it like on a real CPU. Maybe the manual or the help of PLCSim can tell you more about that. regards, |
FCK WAR! |
|
11/25/2015 10:06 AM | |
Posts: 3 Rating:
|
hey mop, actually i already have that document :). First i was used get/put and active connection in s7-400 side seem not working, after that I moved active connection in s7-1500 side also give the same error. Second trial,i tried to open communication with TCON and use TRCV_C. Either TCON and TRCV_C has no error and status "7000" but when i open Network view --> connection, s7-connection status "disconnected" 3rd trial, i want to check communication between s7-1500 and s7-1500 and there is no problem, everything work normal 4rd trial, s7-400 and s7-400 also work fine *Note : for all trial i am not using real PLC, only PLC from TIA PORTAL V13 and Step 7 v5.5 I'm just wondering, is there any issue with PLCSIM? means PLCSIM TIA PORTAL and step 7 v5.5 can't work together
Thanks |