hi Yogendra, connect and parametrize it as 4 wire Transmitter. For channel 0 should the connection be like: terminal9 = "+" terminal5 = "-" terminal1 = measuring wire you also need a bridge from terminal5 to M. See the manual collection of ET200SP. page 1880 for the general terminal assignment of the module and page 4876 for the wiring of current transducers. SIMATIC ET 200SP Manual Collectionhope this helps, regards, |