11/14/2019 3:22 PM | |
Joined: 9/16/2013 Last visit: 1/5/2024 Posts: 511 Rating: (105) |
Hello david_bautista, It is mentioned there AI Energy Meter data sheet, its sampling rate is 2kHz, means 39 samples on 50Hz or 32 on 60Hz. So in total even Sentron PAC3200 is more accurate. Inside manual it is mentioned Accuracy of the line frequency (50 Hz or 60 Hz) is maintained according to IEC 61557-12, and connection via a current transformer is always required for the current measurement. Use toroids with an accuracy class of 0.5, 1 or 3. PAC3200 - Sampling rate 64 samples / cycle at 60Hz PAC4200 - Sampling rate 2048 samples per 10/12 cycles for 50/60H It is necessary at least 10 periods to measure frequency . For 50hz that's 200ms. Once you have frequency of your input signal than you can measure other values correctly(Effective values of current7voltage) |
Last edited by: SOble at: 11/14/2019 15:40:16Last edited by: Jen_Moderator at: 11/15/2019 08:11:17Optimized link. Website: |
|
This contribution was helpful to1 thankful Users |