2/4/2009 7:52 PM | |
Joined: 12/22/2006 Last visit: 1/25/2022 Posts: 1742 Rating: (306) |
Hello, I would start with checking the bus cabling: - termination - schielding - earthing and equipotentials - externallarge consumersthat can induce perturbances in the bus - ... If you have a PG with a CP5611, you could ckeck the bus with the free tool Amprolyzer (using the function Bus status). Itcan be downloaded here: http://support.automation.siemens.com/WW/view/en/18818699 |
Best regards |
|
2/5/2009 6:49 AM | |
Posts: 217 Rating: (52) |
Hello, Also check the hardware digenetic of the CPU. It’ll show why CPU gone to stop mode.Then it'll be easy to find where the problem occurs. |
2/12/2009 4:56 PM | |
Posts: 7 Rating: (0) |
Dear sir, thanks for the reply, I will check for the power cable and revert back about status. thanks®ards kmsd |
6/27/2014 6:47 PM | |
Joined: 3/25/2013 Last visit: 3/21/2019 Posts: 176 Rating: (1) |
New question split intoET200S status when the SF LED flashesand closed. With best regards, Narrator1
|