Hello, From this datasheet (IM151-8 PN/DP = ET200S PN CPU): http://support.automation.siemens.com/WW/view/en/42361392/td Under "Profinet IO Controller" that the CPU supports max 128 I/O devices in standard RT mode. The default I/O update time is 2 msec. To lower the load on thenetwork, you can adjust (slow down)the I/O update cycle of the I/O devices to values matching the real application needs. If for instance 32 msec is enough to react properly towards the process, the bus load will decrease by a factor nearing 16. |