12/8/2016 9:49 AM | |
Posts: 8 Rating:
|
Hello, I have a problem with a hardware configuration using Simatic Step 7 V5.5 + SP3. When I try to compile the hardware configuration I get the error "The system data could not be recreated because the configuration is inconsistent", and when clicking details: "The maximum length of the configuration data for a slave with the PROFIBUS address 23 has been exceeded. The length of the parameter assignment data of slae "(23) ACF" (DP master system 1) exceeds the maximum length specified in GSD file SI05806A.GSE"
https://support.industry.siemens.com/cs/document/21406019/what-conditions-do-you-have-to-comply-with-when-configuring-et-200s-modules-?dti=0&lc=en-WW
Attachmentconfiguration.zip (61 Downloads) |
12/8/2016 1:19 PM | |
Joined: 4/24/2006 Last visit: 5/16/2023 Posts: 8586 Rating:
|
Hello dacuetu, You can search the manual of the used IO cards. for example: SIMATIC ET 200S distributed I/O 2AI I 4WIRE HS analog electronic module (6ES7134-4GB62-0AB0) And see page 9 for more information about 'parameter length' Best regards, Wizard |
This contribution was helpful to
1 thankful Users |