6/18/2020 4:18 PM | |
Joined: 9/27/2006 Last visit: 9/18/2024 Posts: 12282 Rating: (2684) |
Hello Autonix; The ET 200eco PN manual advises that the power cables should be Of a diameter of 0,75 mm2 Technical specifications of the lines Influence of cable length on the supply voltage
Example A 10-m cable with Ø 0.75 mm2 has a resistance of 0.5 Ω, which corresponds with a voltage drop of 2 V at a load of 4 A. Further information on the cables come from the technical data of the cables, and the table provided for the ET 200eco distributed I/O, see the attachment below. The ET 200eco PN proposes a voltage distributor to connect longer lines of the ET 200eco. https://support.industry.siemens.com/cs/ww/en/view/29999018/87908717323 Hope this helps, Daniel Chartier |
This contribution was helpful to1 thankful Users |
6/18/2020 4:40 PM | |
Posts: 2 Rating: (0) |
Thank you for that answer. I will opt for make my own cables with 5G1² and M12 connector to wire for the power supply cable of my ET200ECO. |