Posts: 1547 Rating:
|
Hi Navnag, have you already evaluated diagnostic information from your communication blocks? You can add some programm that will save the additional error inf according to http://support.automation.siemens.com/WW/view/de/9260793/0/enchapter 3.7.3 in case of error. Best is to record several errors including system time in a specific error DB. Or you read in your program in case of error the diagnostic data as given in instruction of Y-link http://support.automation.siemens.com/WW/view/de/1142696/0/enchapter 12.1.3 If this does not help you can monitor subnet of Y-link or your modbus communication with a data analyzer to understand reason of break. |