8/3/2012 4:56 PM | |
Joined: 5/28/2008 Last visit: 4/15/2024 Posts: 4505 Rating: (835) |
Hello,
You can use one of the followings:
|
Last edited by: Ayman Elotaify at: 8/3/2012 4:57 PMAyman Elotaify |
|
3/30/2016 8:10 PM | |
Joined: 1/16/2012 Last visit: 4/26/2024 Posts: 20 Rating: (0) |
Hello, You can use one of the followings:
Hello Ayman Elotaify, As mentioned by erkerl, Is there is any possibilities to use 6ES7134-4GD00-0AB0 (4AI 2-wire) as a 4-wire module? Because I'm using both 2-wire pressure transmitter and 4-wire temperature transmitter. For 2-wire pressure transmitter I've done the wiring as in the manual and it was working. How can I able to measure the 4-wire temperature transmitter signal in the 6ES7134-4GD00-0AB0 (4AI 2-wire) Please suggest Lovins |
3/30/2016 8:32 PM | |
Joined: 9/27/2006 Last visit: 4/26/2024 Posts: 12257 Rating: (2665) |
Hello Lovins; Please read Marcjan's spot-on replies, in this thread: Is it posible to connect 4 wire transducer to 2 wire AI module 6ES7134-7TD00-0AB0? https://support.industry.siemens.com/tf/ww/en/posts/118909/ Hope this helps, Daniel Chartier |