1/12/2018 2:55 PM | |
Joined: 10/16/2007 Last visit: 9/11/2024 Posts: 629 Rating: (45) |
Hello, check the Profibus-adress adjusted on the ET200S and also the wiring of the Profibus-plugs. Regards |
1/12/2018 3:59 PM | |
Posts: 17 Rating: (0) |
Hi, I have already checked it , and it is ok ! I have a question ; Should I define on HW config which terminal module TM I'm using ? Regards |
1/17/2018 4:00 PM | |
Posts: 17 Rating: (0) |
Thank you for help. I did that, but I still have the error. |
1/17/2018 10:06 PM | |
Joined: 1/21/2013 Last visit: 9/4/2024 Posts: 4620 Rating: (707) |
Hello, still BF flashing? |
1/17/2018 10:09 PM | |
Posts: 17 Rating: (0) |
Yes It still flashing and on SF solid red |
1/17/2018 10:11 PM | |
Joined: 1/21/2013 Last visit: 9/4/2024 Posts: 4620 Rating: (707) |
Also on the ET200S BF flashing? |
1/17/2018 10:22 PM | |
Posts: 17 Rating: (0) |
The BF on ET 200S and the BF of CPU are flashing. It gives me on the diagnostic of slave : Error modul on slot 1 and No modul on slot 2 to 13 |
1/18/2018 1:28 PM | |
Posts: 17 Rating: (0) |
Hello, the DIP-switches of the Profibus-address of the slave on the attachment. |
1/18/2018 1:43 PM | |
Posts: 17 Rating: (0) |
Attachmentvideo-1516278916.mov (132 Downloads) |
1/19/2018 3:29 PM | |
Joined: 11/5/2012 Last visit: 8/10/2024 Posts: 487 Rating: (63) |
Hello Sanou. Did you configured Address 8 on your hardware configuration also? Regards. |
1/20/2018 2:29 PM | |
Joined: 1/21/2013 Last visit: 9/4/2024 Posts: 4620 Rating: (707) |
Hello, I not see if you have put the termination module (have a look below) on the right of the terminal module 6ES7 193-4DL10-0AA0 6ES7193-4JA00-0AA0 - Product Details - Industry Mall - Siemens WW do you confirm that you put it? This termination module is included with the IM151-1 16DI / DO - 6ES7 151-1CA00-3BL0 |