Hello laurensvl, The ability to use of anormal digital input module for 1000 pulse/min depends on your system reaction. The 1000/min gives you a pulseevery 62 msec. If you expect your PLC scan cycle + Profibus cycle time to be less that the 62 msec then you can use standard digital input module. What I recommend is to take the safe side and use the ET200S counter module. By using this module you should be sure not to lose a single pulse. Best regards. H-H |