7/21/2010 12:01 PM | |
Joined: 8/22/2009 Last visit: 5/1/2024 Posts: 41 Rating: (1) |
WAITING FOR YOUR HELP |
Veolia |
|
7/21/2010 4:37 PM | |
Joined: 9/27/2006 Last visit: 6/4/2024 Posts: 12260 Rating: (2670) |
Hello Ahmed; Could you please show us where you see the requirement for 330 Ohms as line termination for your 1SI module? Modbus serial standards require a 150 Ohm termination on mutipoint (RS-422 and RS-485) systems, and this is the requirement I have followed on every Modbus line I have setup. Here is a quote from the Modbus over serial lines document, from Modbus.org: MODBUS over serial line specification and implementation guide V1.0 Modbus.org http://www.modbus.org/ 28/4412/02/02 Each line termination must be connected between the two conductors of the balanced line : D0 and D1. Line termination may be a 150 ohms value ( 0.5 W ) resistor Hope this helps, Daniel Chartier |
7/24/2010 7:30 AM | |
Joined: 8/22/2009 Last visit: 5/1/2024 Posts: 41 Rating: (1) |
kindly explain this to me. Attached file is the page talk about 330 ohm line terminator. |
Veolia |
|
Follow us on