8/21/2008 2:43 PM | |
Joined: 12/22/2006 Last visit: 1/25/2022 Posts: 1742 Rating: (306) |
Hello, Normally a power module starts a new powering group, separated from the previous one. See document in annex. The separation is also done at terminal block. Are you sure that you use the correct terminal block for the PM-E F pp ? Should be either 6ES7193-4CK20-0AA0 (screw version), or 6ES7193-4CK30-0AA0. Did you check that? Powering is done at: P: terminal 2or 6 M: terminal 3 or 7 The Load is connected on: one side (P side): 11 or 15 other side (M side): 12 or 16 !!! Be also aware that you use a PM-E 138-4CA01for powering the 4-F-DO. This is only allowed for up to SIL2. For SIL3 you must use 138-4CA50 or 138-4CB11.!!!!! AttachmentET200S-potential distribution.pdf (299 Downloads) |