7/2/2010 3:41 AM | |
Joined: 5/28/2008 Last visit: 4/15/2024 Posts: 4505 Rating: (836) |
Hello Amit_Darwhekar,
Hello KiwiEngineer, The printed wiring diagram under the label is very useful in maintance time. But if you are developing a new project, you may design the wiring digrams before ordering or recieving the modules. So, you should have a manual to draw the correct wiring diagram. I do recommend to have a manual collection. Hope this helps. |
Ayman Elotaify |
|
This contribution was helpful to2 thankful Users |
7/3/2010 12:53 PM | |
Joined: 5/28/2008 Last visit: 4/15/2024 Posts: 4505 Rating: (836) |
Hello Amit_Darwhekar, Short answer, you do not need to bring external +L (24VDC) to terminals of TM of ET200S. Thus because ET200S design is based on not to let users to need extra terminal blocks. So if you have 3 wire proximity switch, you will need +L, -M and signal. you can wire them with pins 1 for DI0, 3 for L+ and A4 for M Please have a look in the table in sheet 3-11 of the manual in my previous post. L+ and M are fed to the terminal module from the bus. Please see this manual of terminal modules |
Ayman Elotaify |
|
1/24/2011 8:45 AM | |
Joined: 3/21/2006 Last visit: 4/25/2024 Posts: 10228 Rating: (1181) |
Hello, There Digital electronic module 8DI DC24V (6ES7131-4BF00-0AA0) and Digital electronic module 8DO DC24V/0.5 A (6ES7132-4BF00-0AA0) Best regards, Hristo Mihalev |
This contribution was helpful to1 thankful Users |
1/24/2011 12:13 PM | |
Joined: 3/21/2006 Last visit: 4/25/2024 Posts: 10228 Rating: (1181) |
For the DI: The logic is - if DI is energized means there is suplied 24VDC. Means on Ax you need to have +24VDC.
4AI I 2WIRE ST analog electronic module (6ES7134-4GD00-0AB0) 2AI I 4WIRE ST analog electronic module (6ES7134-4GB11-0AB0) |