9/15/2023 5:42 AM | |
Joined: 1/21/2013 Last visit: 5/20/2024 Posts: 2798 Rating: (452) |
Hi provence, To be honest, I have never seen this error message. However, I would try as recommended and reinstall the Software Controller. The part number 6ES7677-2DB40-0AA0 is for the spare part, not for the PLC you ordered. Unfortunately, this is a bit confusing because you will find this order number on the unit. The difference is in the licenses that are included. However, according to your memory stick information, you are using a 6ES7677-2SB42-0GL0. So use the following hardware: PC Systems > SIMATIC S7 Open Controller > ET 200SP Open Controller > CPU 1515SP PC F + HMI > 6ES7 677-2SBx2-0xx0. Kind regards |
This contribution was helpful to1 thankful Users |
9/15/2023 12:37 PM | |
Joined: 9/7/2010 Last visit: 9/28/2023 Posts: 50 Rating: (2) |
Hi Stefan, Thank You for answering about this. I wrote this number down/model when it was working in v18 program. it only showed in program and is not on cfast card/et200sp or anywhere? This link is the item I think is correct for CPU. link - https://support.industry.siemens.com/cs/fr/en/pv/6ES7672-5SC11-0YA0/td?dl=en The links you sent - don't know if those will work out? also this link shows what is on controller. 2nd photo bottom of page about corrupt cpu ------- https://support.industry.siemens.com/cs/us/en/view/109768384 Kind Regards Provence |
Last edited by: Jen_Moderator at: 09/18/2023 05:49:28Links optimized. |
|