5/25/2016 12:44 PM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating:
hi Dhaval, have a look in this manual, device specific information->I/O modules->Digital input module DI 8x24VDC HS SIMATIC ET 200SP Manual Collection In chapter 4.2.4 you will find the information. The adress-space of the in- and outputs is an control- and feedback interface in the specified module-manual you will find the a description of the control- and feedback-interface. hope this helps, regards, |
FCK WAR! |
5/25/2016 1:24 PM | |
Joined: 11/29/2014 Last visit: 4/9/2024 Posts: 96 Rating:
Dear, I have configured it but on which input address did i get my count? |
6/1/2016 1:34 PM | |
hi, did you have a look to the manual that I provided? see in Chapter 4.2.4.2 on page 1089 In your case it should be for channel 0: ID 88 for channel 1: ID 94 for channel 2: ID 100 for channel 3: ID 106 regards, Attachmentpage1089.pdf (813 Downloads) |