Dear Experts, I am also facing same problem with ET200SP (Modbus as Master) connected with S7-400 H system. For me, I didnt even get DONE for MODBUS_COMM_LOAD. I am getting error 7000. please give some suggessions or any sample program for ET200SP in S7300/400 system. Thanks in advance. ------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 12/9/2015 12:46:57 PMNew subject after splitting |
|
12/9/2015 2:05 PM | |
Joined: 7/9/2015 Last visit: 6/6/2023 Posts: 3461 Rating:
|
Hi, maybe I do it wrong but 7000 is not an error code, it means function not activ. Please look in the manual of ET200SP PtP communication instructions used on distributed I/O of an S7-300/400 https://support.industry.siemens.com/cs/ww/en/view/69124220 An Application example Master-Slave Communication with Modbus RTU Protocol for S7-300 and ET 200S Systems https://support.industry.siemens.com/cs/ww/en/view/109474714
Regards, Towome
|
If my post was useful, please rate me - thank you! |
|
12/10/2015 9:35 AM | |
Joined: 11/30/2010 Last visit: 5/12/2023 Posts: 39 Rating:
|
Dear All, ET200SP as modbus master with FB640 and FB641 is working now. Error 7000 came, because, we need to add FB611, FB612, FB613, FB614 & FB617 to rectify it. If we didnt add means, we will get "area access error" in CPU diagnostics and block will not be enabled. Got this block in P2P communication in this link here are the blocks for STEP7 V5.5 In addition to that, we need to enter actual baud rate (9600 in my case) in FB640. I had entered value 6 (for 9600 baud rate) as in manual. Now, modbus is working fine. Thanks for your support. Regards, S.Narayanaswamy |
This contribution was helpful to
1 thankful Users |
9/13/2016 6:08 PM | |
Posts: 9 Rating:
|
Hi S.Narayanaswamy, Can you please share project backup. |