8/15/2016 8:56 PM | |
Posts: 52 Rating:
|
You mean in TIA selection Tool? I did not get that one to work with the central rack, do you have any example on this? |
8/16/2016 2:57 PM | |
Joined: 5/6/2010 Last visit: 5/26/2023 Posts: 1882 Rating:
|
Hello ASIMO99, at the attachment you will find a sample project. I hope this is helpful. regards AttachmentSample_procject.zip (178 Downloads) |
8/17/2016 8:16 AM | |
Posts: 52 Rating:
|
first I would like to thank you for your efforts to help those in need on this forum. I have included a screenshot of your TIA selection tool program, my issue lies inside the ET200MP and ET200SP racks, I need to see how many PMs do I need for the cards I have installed. Please see my attached example, would 2 power modules be enough for all the cards I have selected? and how can I determine if it is for my future projects? thank you very much AttachmentSample_S71500.zip (149 Downloads) |
8/17/2016 11:28 AM | |
Joined: 5/6/2010 Last visit: 5/26/2023 Posts: 1882 Rating:
|
Hello ASIMO99, I know what you want to see at the configuration. Please look at the attachement, there are 2 pictures, one with out error and one with error. I hope this is that what you want. regards AttachmentPictures.zip (169 Downloads) |
8/17/2016 12:51 PM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating:
|
hi ASIMO99, note that in the ET 200SP you don´t need a PM. The power supply of the modules are over the BaseUnits. See the ET200SP System manual in the manual collection: SIMATIC ET 200SP Manual Collection hope this helps, regards, |
FCK WAR! |
|
8/17/2016 3:54 PM | |
Posts: 52 Rating:
|
Thank you for your reply. What about ET200MP ? |