6/28/2018 10:52 AM | |
Posts: 15 Rating: (0) |
Dears I would like to ask the difference between ET200SP and ET200M as Remote I/O System via Profibus. Thank You! Best Regards, Daisy |
6/28/2018 1:13 PM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating: (1054)
|
hi, ET200SP is smaller and has an other mounting system on cap-rail. It is a newer system family and its controller are from the S7-1500 series. SIMATIC ET 200SP Distributed I/O system chapter 3.1 ET200M is based on the S7-300 system and has an own mounting rail. Most of the IO-modules of S7-300 are suitable for the decentral ET200M-Interface-Modules. SIMATIC Distributed I/O device ET 200M chapter 1.4 hope this helps, regards, |
Last edited by: mopS04 at: 6/28/2018 1:16:13 PMFCK WAR! |
|
This contribution was helpful to1 thankful Users |
2/18/2021 5:38 PM | |
Joined: 9/1/2017 Last visit: 7/9/2024 Posts: 156 Rating: (19) |
Hi
1) you can find both profibus dp and profinet interface module for both et200m and et200sp 2,3) there is various safety signal modules (sil certified) for both system. Et200m uses most of s7-300 modules and it's very common in safety related applicatins utilized by s7-300f/400f/fh cpus. There is also Et200sp fail safe controller based on s7-1500 cpus. Regards Hosein |
Last edited by: Jen_Moderator at: 02/19/2021 09:37:21Optimized link. |
|