6/13/2007 7:52 AM | |
Posts: 17 Rating: (0) |
Thanks for your reply. I am trying to contact Etel support department to get the data for SIMODRIVE. |
6/19/2007 7:45 AM | |
Posts: 17 Rating: (0) |
Dear Sir: We are now setting up Etel motor combined with SIMODRIVE 611U(speed control module). We used the dataEtel send to us, but always 610# alarm( Rotor position identification has failed ) after enable the drive. And MD1734=-2, it means " Current was not able to be reduced again in time during the measurement Remedy: Check armature inductance (P1116) and if required, increase " we also tried increase MD1019(Current, rotor position identification), but same alarm, if too high, alarm 612# The customer select incremental encoder, so we use MD1075=1 (Rotor position identification based on saturation). Motor type: TMB0360-100-3VBN Is it possible to use the method to identify rotor position? If yes, any other machine data have to be set? Thanks. AttachmentSI-TMB0360-100-3VBN.pdf (573 Downloads) |
7/20/2007 11:58 AM | |
Posts: 17 Rating: (0) |
Dear Sir: The motor now can hold the position but 607# alarm when set speed. The attachment the 611U data, could you give me some idea? Thanks. Liu Tong Attachment611U_Etel.zip (702 Downloads) |