Hello. I already have comunication with NetPro, but I would like to do this communication without NetPro, in other application I have made communication between two CPU 317 2PN/DP but my trouble is whenI try to do communication with one CP317 2DP/PN an one CPU 317 with CP 343-. I atacch S7 program ith configuration that I have, hope this can help us. AttachmentPlc1_1.zip (106 Downloads) |
4/14/2009 4:15 PM | |
Posts: 13 Rating:
|
Atacch Program PLC2
AttachmentPlc2.zip (133 Downloads) |
4/17/2009 7:22 AM | |
Posts: 382 Rating:
|
Dear jeme, In your attachment of PLC1 & 2 I didn't able to see your Hardware configuration nd netpro config. Thus i do not know where you went wrong. However i have attach an example base on what you have describe earlier. Asonly one ofyour CPU317has CP343-1 thusyou can't establish ISO-on-TCP connection in the netpro.You need two CP343-1 one at each CPU317 then you can have ISO-On-TCP connection in netpro. As for your case you canuse S7-connection [see my example] Using S7-connection you can using some of the blocks to transferyour information i.e Bsend,Brcv,Get,Put,etc. Hope this link helps. How do you program communication blocks FB12 "BSEND" and FB13 "BRCV" for data exchange on the S7-300? By the way change the extension of my zip file to rar if you can't open Hope this help with regards, how come? AttachmentExample.zip (169 Downloads) |