1/8/2010 7:24 AM | |
Joined: 9/28/2005 Last visit: 12/10/2024 Posts: 2957 Rating:
|
Hello, This topic was discussed many times allready. At S7-300 side you use AG_SEND/AG_RECV functions and type of communication is TCP. Don't forget to set active connection estabilishment at S7-300 side ! I never get it working by passive estabilishment at S7-300 side. At S7-1200 side you just configure connection to unspecified partner and use TCP protocol. S7-1200 side is the same program as from example here, but just take one PLC and change partner to unspecified. |
Best regards, |
|
1/8/2010 3:00 PM | |
Posts: 32 Rating:
|
Thanks for your help, I'll try. |
5/15/2014 8:11 PM | |
Joined: 4/21/2006 Last visit: 1/27/2025 Posts: 510 Rating:
|
New question was splitted to a new thread: TIA V13: Ethernet Communication between S7-300+CP343-1Lean and... |