7/17/2013 7:52 AM | |
Joined: 10/11/2006 Last visit: 2/1/2023 Posts: 5410 Rating:
|
Hello viralpatel, this port does only support acyclic connections (S7 protocol), see here. So you may use it with acyclic communication toHMI, but not for cylic communication with PLC. |
With best regards, |
|
This contribution was helpful to
1 thankful Users |
7/18/2013 2:22 PM | |
Posts: 319 Rating:
|
Hello TechTeam, If the On board Ethernet port on CU 320 2 DP supports S7 communication, can i use it for OPC communication (My PC will have an OPC Server and it will try to access data from CU320 2 DP)? Thanks and regards, nand gate.
|