10/22/2012 3:55 PM | |
Posts: 139 Rating: (5) |
Thanks for your detail and helpful reply. i have enclosed siemens example i have read. As my understand, example is showing configure message number itself? Sorry i am totally confused on that. AttachmentFAQ.pdf (290 Downloads) |
10/22/2012 4:47 PM | |
Posts: 836 Rating: (99)
|
Hi, in PCS 7 you never create EV_ID by your own. If you call a ALARM_8P block inside an other block you have to do following: You have to create inputs for each ALARM_8P you are calling inside your own block. You have to give some relevant S7 attributes to those inputs. When you are calling the ALARM8P block inside, assing the input to the parameter EV_ID. When you are compiling the CFC programm, the compiler will write the correct EV_ID to those Inputs and the ALARM8P will be called with the correct, automatically created EV_ID. Check out this FAQ for the details: |
This contribution was helpful to1 thankful Users |
10/23/2012 2:20 AM | |
Posts: 139 Rating: (5) |
Hello Bob, I am customising block and after read some, that thoughts (confusing) came to me. Thanks for nice explanation and FAQ. |
10/30/2017 1:18 PM | |
Joined: 6/19/2017 Last visit: 4/25/2024 Posts: 7959 Rating: (162) |
New question published by Pendalf is split to a separate thread with the subject Some messenges coming incorrect - why?. Best regards |