11/5/2014 11:39 AM | |
Joined: 1/17/2007 Last visit: 10/6/2020 Posts: 289 Rating: (3) |
Anybody has seen this error ? 34 of 50; Event ID: 16# 02:4016 CPU info: Serious hardware inconsistency (not relevant for user, system code: 16#00644A4E 16#10000034, RID=16#030D0000) CPU changes from STOP (initialization) to DEFECTIVE mode |> HW_ID= 52 - Operating mode control The PLC goes into STOP mode. Only after complete download can it be put to RUN. Error appearead at POWER ON. TIA V13 UPD5 Thank you. AttachmentDiagnostics.pdf (104 Downloads) |
11/7/2014 3:57 PM | |
Joined: 7/7/2010 Last visit: 3/28/2024 Posts: 14520 Rating: (2332)
|
It appears you are using an external memory card. Try this: 1. Remove the memory card 2. Power cycle the PLC 3. Reset the plc to factory defaults using the online & diagnostics menu 4. Compile / rebuilt all for your PLC hardware and software. 5.Download just the hardware configuration. Right click on the PLC, and select Download. Then select download hardware configuration only. 6. Start the PLC 7.Check the diagnostic buffer. If it is working fine, your hardware configuration is acceptable. If you need to fix the hardware config, make sure all firmware revisions match your project for each module. Once your hardware download is acceptable, download the software configuration. Check the diag buffer again. If it looks like it did in the original post, forward your project with exact list of module part #'s to Support Requestso they can offer further suggestions. |
science guy |
|
10/26/2015 7:31 AM | |
Joined: 3/21/2006 Last visit: 3/26/2024 Posts: 10228 Rating: (1180) |
Hello, I would also suggest you to contact Support Requests. Best regards, Hristo Mihalev |