Industry Online Support
Technical Forum
8/14/2012 12:28 PM | |
Posts: 59 Rating: (2) |
Hi All Executin System and SystemInterruptTask have ExecutionFaultTask in.So What is the ExecutionFaultTask? What Can I do it, How can it use? Thanks.
|
8/16/2012 8:07 AM | |
Posts: 59 Rating: (2) |
System is Simotion. Best Regards
|
8/16/2012 10:23 AM | |
Joined: 5/12/2006 Last visit: 9/20/2024 Posts: 22365 Rating: (3011)
|
Hello, the executionFault Task is for any exception in userprograms. Execution errors in programs You set the response to execution errors in programs in the task configuration. This affects the following operations, for example: Invalid operation with floating-point numbers (e.g. logarithm of a negative number) Incorrect type conversions Division by zero Violation of array limits Normaly the CPU goes to Operation Mode Stop, when you use the Execution Fault Task then you can handle this exception from user program an the CPU must not go to STOP. More Informations you can get in the SIMOTION Manual "SIMOTION RunTime Basic Functions" Download: http://support.automation.siemens.com/WW/view/en/60744985 Regards Christoph |