Hello Allun; If you are using an incremental encoder then you could try simulating it with a ramp function, such as this one provided in a Siemens FAQ: http://support.automation.siemens.com/WW/view/en/1853767 We have used it successfully is an earlier project. We started by using a scope on the encoder signal lines to make sure of the input values to the PLC so we could simulate them later. If you have an absolute or gray-scale encoder, then you would probably have to build or modify the ramp values so they match the increasing values as your program expects the real one to dio. Hope this helps, Daniel Chartier |