Hi, apologies for delayed response, please see attached, the trace is of the Sinamics external encoder object at the highest trace clock cycle. I also attach the fault buffer in relation to the laser, there are no other alarms/faults prior to this occurring. The Sinamics fault is F31112 Encoder 1 signals an internal error (1) The bottom bit track is Fault and the one above is Alarm, You can see however, that there does not appear to be any strange events occurring. The laser module communicates via SSI absolute protocol to the SMC30 module. At speeds below 9 metres per second, the encoder objects have never failed. We are well within scope of the laser in terms of max speed, acceleration and range, but as You can see, the data is still being acquired by the SMC, but because the Sinamics object faults, the TO then freezes. Regards, Graeme AttachmentTrace_Graphic.zip (515 Downloads) |